Errors are appearing when we try to open assigned modules of Simulation Pro+
Best Regards,
Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast
HI,
The first error seems to pointing to that there are multiple users accessing the same module at the same time.
Are there also a PRO station installed or can you access the modules from the OP stations.
Is the module open in some other window/ computer?
The #2 and #3 error is pointing to the databse files, if the harddrive (virtual drive) is OK then it´s propably that the database is corrupted.
You could try to run the "fix database tool" and see if that helps.
Error #4 and #5 is pointing to same as error 2 and 3.
Is this message appering in every module or just some modules?
If you have the backup FHX-file, import it and try if that one works.
If the problem is only one module, you could try to open the FHX file and take a look on it and compare it to a working block.
What is the system layout...? versions etc.. have you installed all the updates and hotfixes, is the SQL running...?
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
nikfly@gmail.com
In reply to Niklas Flykt:
Smells like database corruption. Did you have power failure recently? Or ProPlus was not shutdown properly?