Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5478 subscribers
Views
8038 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Diane Barkin
12 Aug 2025 12:09 AM
SIS License for Small Engineering Firm
0 Replies
laurent maurer
10 Aug 2025 11:58 AM
Deltav Excel Addin in Deltav 15
6 Replies
Jim K
9 Jul 2025 9:04 PM
DeltaV Live Duplicate Displays
0 Replies
Caleb Holland
30 Jun 2025 12:07 PM
DeltaV V13.3.1 AI Card 4-20mA HART IO Card SV dropping out intermittently
0 Replies
Mark Bendele
11 Jun 2025 7:26 PM
Diagnostics Report
1 Reply
<
>
Similar Posts
DeltaV Live - Restore Database Error Message
BulkEdit error message: WARNING: Required data does not exist on line 2 - module_name
Assistance Request for DeltaV Error Messages (See screenshots)
Eleborate the SK_CANTINSTALLHOOK error message
Verbose error messages in VBA
Share
Not Answered
DeltaV Live error message-does anyone have any idea about the error message?
1 Reply
Joshua Granger
10 Mar 2023 5:25 PM
Any given user can only have one instance of DeltaV Live running at a time. If you are able, log in as an engineering account (i.e. dvmanager) and go to the Windows Desktop. From there, open Task Manager, go to details, and close all open instances of the DeltaV Live process (I don't recall the executable name). Then, log back into the account you are trying to use and try opening DeltaV Live again.