Not Answered
DeltaV Live error message-does anyone have any idea about the error message?
1 Reply
Joshua Granger
10 Mar 2023 5:25 PM
Any given user can only have one instance of DeltaV Live running at a time. If you are able, log in as an engineering account (i.e. dvmanager) and go to the Windows Desktop. From there, open Task Manager, go to details, and close all open instances of the DeltaV Live process (I don't recall the executable name). Then, log back into the account you are trying to use and try opening DeltaV Live again.