SIS tools

Gents

Could you please advise if there is any tool we can run to collect the  SIS reference parameter, also tool for collect the bypass voter on the system 

Thanks

1 Reply

  • Hello Hassan,

    Short answer is, yes.
    Could you please expand a little bit on what are the requirements?

    Cross reference are provided by Control Studio on a Control Module by Control Module basis, all bypasses and forces are captured by the SOE, and can be easily filtered, in addition, DeltaV Mobile allow for SIS bypasses and forces monitoring, while allowing for the creation of specific profiles to receive notification, so the information is pushed to the right team or person.

    Hope that helps, let me know if you have additional questions.

    Rgs,