Emerson Exchange 365
Sign-In / Register
Site
Sign-In/Register
Community Hubs
DeltaV Community Connect
Ovation Users Group
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
Perspectives
Emerson Automation Experts
Conferences
San Antonio 2025
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Services
Services Forum
Electronic Marshalling
Services Forum
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Services Discussions
Scott Ross
25 Sep 2018 7:15 PM
Save re-wiring your legacy termination / marshalling panels using FlexConnect Solutions to migrate your legacy DCS to the DeltaV DCS
0 Replies
MC_Chow
24 Sep 2018 5:47 PM
Is there a SIS in your BMS?
0 Replies
<
Similar Posts
Creative use of Electronic Marshalling
Modernization of DCS and PLC with Electronic Marshalling
Modernization of DCS and PLC with Electronic Marshalling
VIDEO: How Electronic Marshalling reduces project schedule risk
VIDEO: How Electronic Marshalling reduces project schedule risk
Share
Not Answered
Electronic Marshalling
How different is this than universal inputs?
Regards,
Brian
1 Reply
Andre Dicaire
6 Oct 2017 7:19 PM
Are you referring to Universal IO?
UIO is touted as the same so it can be difficult to see the difference based marketing material.
Both products allow you to configure each channel to be any supported signal type. But that's about it a star being the same. UIO supports 4 signal types, AI, AO, DI, DO. All are high side powered signals, no isolated inputs,all 24VDC.
Electronic Marshalling allows you to not only software configure the channels, but also hardware configure to match filed signal/device.
There is a dedicated terminal block and distributed field power for 3 and 4 wire devices and ability to power with DC or AC Discrete devices.
And the CHARM allows you to disconnect from field wiring.
We have native IS CHARMS for hazardous areas.
CHARMS can directly support over 30 field signals with out requiring interposing relays or Signal converters.
It is far easier for me to explain how they are the same.... They are not the same!
Lastly, and maybe most importantly, Electonic Marshaling allows you to add CPU capacity to the existing IO, which eliminates ever leaving spare IO or IO space unusable. A new controller can be added to implement new control modules leaving all existing IO assigned as is.
Between what I call IO Diversity and Expendable CPU, these products are very different.
Andre Dicaire