Alarm Total in Alarm List

When the filter is used on Alarm list so that only certain priorities are shown, is there a way to have to total number at the top represent the total number of alarms remaining after filtering?

  • Kent, If you turn on the Status bar on the Alarm Summary ActiveX object it should show the correct number of items.

    Right Click on the Alarm Summary object and select Properties

    Then select the layout tab and check the status bar

    Then at the bottom you will see the counts. I have seen the counts that are using datalinks be "stale" and require the picture to be reopened to get the correct values but the status bar seems to always be correct.

  • Thanks.  I had the  Alarm Summary Active X positioned such that the status bar was sitting under the Alarm Banner since I did not know that it was there.  Now I know. 
     
    This is a very valuable resource.
     
    Thanks again.
     
    Kent E Mitchell, P.E.
    92-H PRC
    Bartlesville, OK 74003-6670

    918-977-4654 office
    918-977-7520 fax
     
     
    Confidential Information - This email is for use by the intended recipient(s) and may contain privileged, confidential or copyrighted information.  Unauthorized use, copying or distribution of this e-mail, in whole or in part, is strictly prohibited.  If you should not be an intended recipient of this e-mail, please notify the sender by return e-mail and delete this e-mail.