I would like to create a graphic to show the operators all the alarms that have been shelved by the operators. I would like it to filter out the alarms that are suppressed by logic. This would allow the operators to see a list of the alarms that have been shelved by an operator only. What would be the recommended way to do this?
In reply to Matt Stoner:
In reply to Kent:
There is no option to filter on the SUPRSN but the SUPRSN is shown as a column on "AlmSupp" graphic but yes I would recommend moving the logic to use OOS as well as adding the setting the SUPRSN to "Suppressed by Logic" (which would be Visible but not User Selectable in the dv_alm_sup_rsn named set) or something else you want. I think this "Suppressed by Logic" will come in v13.3.1 as a default at index 7 if it isn't already in v13.3, I can't remember if I updated my 13.3 copy because I was working/testing the new alarm management modules coming in 13.3.1. You would then create a new display starting from AlmSupp and change the options I described above to get what you are looking for.
Make sure that you set the Field Security for OPSUP, SUPRSN, SUPTMO and OOS to the appropriate levels which I suggest changing from the DeltaV defaults of Restricted Control for all except SUPTMO.
Regards