Is there a way to observe the outgoing traffic of DV OPC Server or even a Log file?

Hi all,

we have a OSIPi OPC Interface running collecting data in "advise" (If the value changes,  the OPC sends an update of the value) mode from our DeltaV OPC Server. For some tags we are not receiving value updates. Is there a way to observe the outgoing  traffic from the OPC Server to Pi-Node? I was thinking in a log file or something similar in order to check that the OPC is definitely sending the update. Because in the OSIPi Interface log i can´t see an update for the value.

If i request the value with OPC-Remote Tool i can see the updated value, therefore i think there could be a problem with the OPC "sending" the value update. Same if the tag is switched to "polled" (a request to the OPC Server to send an update), i can see the updated value. For Performance reasons i want to use the first explained "advice"- mode.

Greetings

Tobias

  • First, make sure you're not trying to mix advise and polled tags in the same PI interface. There are some discussions in the PI documentation where it describes the location codes.

    Do you have the deadband set properly in DeltaV for the value you are trying to use "advise" updates with? I think PI uses the same deadband as the DeltaV Historian. Pay attention to the units for the deadband setting.

    This is all from memory...
  • In reply to Walter Wilson:

    Unfortunately, there is no logging capability to see what is being sent from the DeltaV OPCDA server. Also check to see if this problem is just for certain types of tags (strings, integers, etc.). Just FYI, we are examining improving the logging capability for the DeltaV OPC Server in future releases to help these types of troubleshooting activities.
  • In reply to Walter Wilson:

    We are using advice tags only, i read this in the PI documents also. We are not using the DeltaV Historian, the data archive is realized in Pi, therefore the deadband is configured in Pi. Thanks for your fast reply!
  • In reply to Brian Crandall:

    Thanks for the hint about the type of the tags i will check this also. Good to know you are working on the logging capabillity, it sure will be helpful. Thanks for the fast answer.