Hello,
I'm doing a project to convert all 90-70 to rx3i but, i have to enable communication(using CCM master and slave protocol) between a 90-70 and a Rx3i PLC. The commreq function blocks return a status code "5890" but i found nothing about this status code. Anyone know what is the meaning of this error code ?
thanks,
Fred
I am assuming that the 90-70 side you are using IC697CMM711 as CCM protocol master, RX3i side IC695CMM002/004 as CCM slave, in the RX3i side, there is a tab "PortData_CCM_Salve1", you have to assign Ref Length for CCM slave
In reply to Jimmy Lee: