Hello Everyone,
Is there a guarantee that all instrument vendors implement the STATUS_OPTS correctly? We have a Brooks flow meter where we'd like to ignore the instrument going out of range, but in our experience the status of the PV is set to Uncertain even if "Uncertain if Limited" is unchecked.
Our problem is that this triggers a module alarm on the totalizer that's linked to the flow meter. Also, the totalizer does not totalize an Uncertain value. Both the AI and the totalizer module is based on PCSD.
Any best practices on how to avoid this?
Andre Dicaire
In reply to Andre Dicaire:
Hi Andre,
Thank you for explaining that the Limit Status is separate. This is Foundation Fieldbus though, not HART, so the function block is running in the instrument itself. This is what we found in the manual of the instrument, a bit confusing for me: