Expression

Hi All

If i have ACT block with four line for expression inside it,how can ignore or pending  one of them from execution but without delete it  

  • Hi Hassan,
    You just have to enter "REM" in beginning of the line which needs to be ignored. For example:-
    OUT1 := IN1.CV This line needs to be ignored so you enter
    REM OUT1 := IN1.CV

    Note:- However this will only ignore that particular line number. If you want to ignore a whole set of expression, then

    OUT1 := IN1.CV ;

    OUT2 := IN2.CV ; To ignore this expression you can do this

    (* OUT1 := IN1.CV ;

    OUT2 := IN2.CV ;  *)