Emerson Exchange 365
Search
Sign-In / Register
Site
Search
Sign-In/Register
Services
Products
Control & Safety Systems
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
IIoT & Digital Transformation
Industries
Chemical
Food and Beverage
Industrial Energy
Life Sciences
Oil & Gas
Power
Refining
Other Industries
Women in STEM
Events
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Nashville 2019
San Antonio 2018
The Hague 2018
World
China
South Korea
Russia
More
Cancel
Products
More
Control & Safety Systems
DeltaV Forum
ALARM HORN PROBLEM
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Control & Safety Systems Discussions
Douglas Crowder
1 Apr 2024 5:20 AM
How to remove Live button from Flexlock
1 Reply
TreyB
28 Mar 2024 4:57 PM
Local accounts after joining domain
10 Replies
TreyB
27 Mar 2024 5:48 PM
Remote Desktop only working on Primary ACN
5 Replies
frankfu
27 Mar 2024 3:02 PM
loss communication between redundancy DeltaV PK and redundancy Ehternet/ip every 5 minutes?
0 Replies
TreyB
15 Mar 2024 9:33 PM
GEM broke my displays
1 Reply
<
>
Similar Posts
Alarm Horn Retrigger
ENABLE HORN FOR ALARM
Alarms, acknowledging and silencing horn
Alarm Question/Plant Horn
Link DO Module (Audible Horn) to Area Critical Priority Alarms
Share
ALARM HORN PROBLEM
Hello..gm
Actually, i have a problem on site. I have EWS, OWS-1, OWS-2, OWS-3 stations are present on site. In this plant two areas are there Formaldehyde (FD) & Hexamine areas.
This is the DCS Upgradation project. Upgradation procedure work is completed.
Base version=10.3.0 & Upgraded version =13.3.6 (R6).
So, the issue is i'm facing is on alarm banner horn problem. i have only properly getting all both area's alarm horn on OWS-3 only. Remaining station only FD area's alarm horn generate on alarm banner. Hexamine is not.
I have notice on my remaining station that horn is not visible on alarm banner when hexamine alarm is come.
I have tried following things to rectify.
1). Replace Graphics iFix, pic, download ans yellow page folders of ows3 in remaining operators stations.
2). Replace the Alarm banner.
3). Reassigned Area's on Alarm&Event (Area_A, FD and Hexamine).
4). Formatted and Reinstalled 13.3.6 (R6)
5).Rerun the system also.
Thanks & Regard
SUMIT PATIL
8982092906
2 Replies
Matt Stoner
12 Nov 2018 2:49 PM
Look on the AlarmFilter display, do you see white check box with a check mark on the areas?
If you see a grayed out box on the area(s), login to DeltaV again with DeltaV Login button on toolbar or from DeltaV Logon button from Flexlock.
Sal Salamone
12 Nov 2018 11:04 PM
In reply to
Matt Stoner
:
Hi Sunit,
In addition to what Matt suggested, check to be sure the alarm areas have been added to the non-working workstations; under Alarm & Events. To do this, open DeltaV Explorer, expand one of the workstations having an issue, and left click on Alarms and Events. In the right hand panel you will see all the areas included to that workstation; right click to add an area. A workstation not being included in the Alarms and Events will also prevent it from making operational changes to equipment in that Alarm Area as well. The Alarm Areas are the groups you set up under Control Strategy. AREA_A is there by default.
Hope that helps.
Sal
Sal Salamone