Hi experts,
What's the common solution for PID loop interlock?
A sequential control example, there is an interlock which requires flow control valve locked in 15% until the flow reaches 300 sqf/h during downstream pump startup; after pump is confirmed running, switch the flow control to AUTO.
Another example, once the interlock is active, force valve to close or any position which the process requires, when the interlock is clear, need manual reset.
Thank you very much for your time and your considerations.
J
In reply to Abhinav Thakur:
Thanks Abhinav and Tyler.
I tested today by setting Track_In_D = TURE, Track_Val = 5 (TRK_SCALE: 0 - 100) when PID mode either in AUTO or in MAN, PID/OUT didn't change at all. Is there any additional parameter need to set? Thanks.
In reply to Jiye Yuan:
In reply to john_doe030488: