Hello,
While commissioning the controller i do have an error saying SD plus 11.3 does not match the configured controller model SD plus 11.3 or DeltaV system 12.3, you must upgrade the controller hardware to the current system revision before proceeding with the download.
if selected to proceed with the commissioning it takes a way long time some times and some time it gets failed saying auto sense failed you may need to download your workstation.
should i upgrade the controller ? or even though i continue how would i get it running.
any help is appreciated.
Thanks
Hi Rahul,
What is the version of your DeltaV system? Your error message indicates one of a few things:
Please verify these two items. In the case of this mis-aligned software revisions, you must commission the controller and then use the controller upgrade utility to flash it to the correct software revision.
Dave