Dear experts here,
Currently I am working on a Closed-Loop Setpoint Response tuning method which need me to switch the PID controller to Proportional-Only. What is the right method to get this type of controller? Set the RESET to 0 in order to disable the integral? Or is it necessary to change the STRUCTURE parameter at the PID block to "P on Error, D on PV"? Currently at DCS, the settings is "PI on Error, D on PV". I tried to change the settings into "P on Error, D on PV" to disable the integral action. But when I turn the controller from manual to Auto, suddenly the controller output goes to zero. It caused an upset to the process. I am not sure what is the problem, because before this no such problem occurred in the plant. Can anyone here provide me the correct procedure to get the P-Only controller? Thank You.