Is there a way to keep the value of Totalizer intact instead of initializing to zero after cold re-start period has expired in SQ controller? I have enabled the NVM memory for the Integrator block and the control module, but the totalizer value goes back to zero whenever SQ controller is power up after the cold restart period.
Regarding your statement
"the totalizer value goes back to zero whenever SQ controller is power up after the cold restart period"
The purpose of the cold restart memory period is to define when information is to be discarded after being powered down. From BOL:
"... if the specified time elapses before power is restored, the controller goes into the USERRESTART state. This state requires you to download the controller node from the Explorer."
(http://www3.emersonprocess.com/systems/support/bol1131/source/extfile/b_theory/html/controller_restart.htm)
If you ket the cold restart time elapse, the values will be cleared.
The Integrator block (totalizer) preserves the following parameters. I assume you have selected 'Restore Parameter Value after Restart' on OUT.