Water density calculation given pressure and temperature.
Does anyone have a function block or method to calculate density of water given a presssure and temperature?  The STM function block is only valid for superheated and saturated steam, not liquid water.
  • Water density in the temperatures 0°C - 100°C
    Temperature oC
    Density g/cm3
    Temperature oC
    Density g/cm3
    0
    0,99984
    20
    0,99820
    1
    0,99990
    2
    0,99994
    22
    0,99778
    3
    0,99996
    4
    0,999973
    24
    0,99730
    5
    0,99996
    6
    0,99994
    26
    0,99679
    7
    0,99990
    8
    0,99985
    28
    0,99624
    9
    0,99978
    10
    0,99970
    30
    0,99565
    11
    0,99960
    35
    0,99404
    12
    0,99950
    40
    0,99222
    13
    0,99938
    45
    0,99022
    14
    0,99924
    50
    0,98805
    15
    0,99910
    60
    0,98322
    16
    0,99894
    70
    0,97779
    17
    0,99877
    80
    0,97181
    18
    0,99860
    90
    0,96532
    19
    0,99841
    100
    0,95836
    Niklas Flykt
    Klinkmann Oy
    nikfly@gmail.com
  • In reply to Niklas Flykt:
    These laws would be useful if I needed equations relating to gases.  My original request is for a function block for water.  I have used Rockwell PPax and they have a function block using Steam tables to determine properties for conditions including water phase, saturated steam and superheated steam.  DeltaV has a PStm function block but this does not provide values for liquid phases.  My nominal operating conditions will be 80 deg C and 1 Mpa, but can vary any where up to 1.2Mpa and above ambient temperature.
  • In reply to ktyang:
    "These laws would be useful if I needed equations relating to gases."some of  these laws also apply to liquids.
    Could you give some more information about the process you want to measure.
    The weight(mass) of the water stays the same, only the volume changes when the temperature changes.
    If you use a PD measurement then you will get the correction automaticly ?
    If you use height measurement then it´s and other thing..
    Niklas Flykt
    Klinkmann Oy
    nikfly@gmail.com
  • I don’t know the application that spawned the original request, but happened on the same need for water density, recently.  It was a waste heat steam generator application and we had to provide 3 element steam drum level control.  There is more than one way to configure this, of course, but we were essentially using feed forward to the level controller PID loop effectively ratioing boiler feedwater volumetric flow (GPM) to produced steam mass flow (KPPH).  We had to provide a feed forward gain and it depends on the density of the boiler feedwater.  In our case the temperature doesn’t vary enough to warrant dynamically updating the FF gain, but in some applications it might.
    Lou Heavner
    Lou Heavner | Consultant, Industry Solutions
    Emerson Process Management | 1100 W. Louis Henna Blvd. | Round Rock | TX | 78681-7430 | USA
    T +1 (512) 834-7262 | M +1 (512) 406-1457 | F +1 (512) 832-3476 | Lou.Heavner@Emerson.com
    From: Niklas Flykt [mailto:bounce-nikfly@community.emerson.com]
    Sent: Friday, April 19, 2013 2:44 AM
    Subject: RE: [EE365 DeltaV Track] Water density calculation given pressure and temperature.