Hi ALL
i am just trying to find out a way to figure out how much is left on SD plus controller free time
DV is V11.3.1
thanks
There are a few ways to view controller free time. The simplest is to open diagnostics and click on the controller, it will be there under the listed parameters. You can also right click on the controller in diagnostics and get a more in depth view via the time utilization chart. If you are looking to trend this over time you can also build a controller monitoring module and an external reference parameter to controllername/fretim and add the tag to your historian. You should also be looking at idle time as well and make sure it is not dropping. Is there a particular issue you are troubleshooting? There are a lot of factors at play when looking to gauge controller loading. Controller redundancy and CHARMs are 2 that have a big factor on reommended freetime.