How To Alert on Power Module Life

During Exchange today, I had lots of conversations about the best way to know if a power module is getting low and should be replaced.

We HIGHLY reccomend NOT tracking battery voltage and setting alerts.  First, the voltage curve is not linear - its fairly flat until the very end when it drops quickly.  Second, each device uses a different about of power, so the alert levels are device dependent.

There are two alerts sent for Emerson Smart Wireless Devices - a warning, which indicates that the power module should be replaced soon and a Critical alert, which means that it should be changed immediately.  For the Rosemount Wireless products, a device will stop reading the sensor on a critical alert;  however, it will keep transmitting data for the rest of the mesh.

If you are mapping for OPC/ Modbus:

Rosemount, Vibration, Analytical Devices:  

Low Warning alert tag:  POWER_SUPPLY_CONDITIONS_OUT_OF_RANGE   (Boolean)

Critical Alert:  CRITICAL_POWER_FAILURE   (Boolean)

Fisher 4300 Series:

Low Warning Alert: BATTERY_WARNING_GETTING_LOW

Critical Alert:  CRITICAL_POWER_FAILURE

These alerts are easy to use and provide a better indication of power module status.