Recent Valves, Actuators & Regulators Discussions
Jim Cahill
29 Feb 2020 5:49 PM
HART feedback from a Fisher DVC 6200 PD Valve Positioner for Ovation
1 Reply
mark.nymeyer
19 Feb 2020 2:20 PM
Article: Valve Proof Test Credit for Process Trip: Processing January 2020
0 Replies
mark.nymeyer
13 Jan 2020 4:26 PM
Article: Purchase a Qualified Valve for Your Application
2 Replies
mark.nymeyer
3 Oct 2019 11:35 PM
Article: Testing Slurry Valves for Reliability, by Tim McMahon, Emerson
1 Reply
Emerson Exchange News
1 Oct 2019 9:04 PM
High performance valve solution ensures safety for Koch Ag
0 Replies
<
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.