Recent Valves, Actuators & Regulators Discussions
Saurabh Bhardwaj
24 Apr 2020 9:27 AM
Butterfly valves for Cavitation Service
0 Replies
Saurabh Bhardwaj
23 Apr 2020 2:50 AM
Control Valve-Flashing Service-Velocity at the Valve exit
2 Replies
mark.nymeyer
8 Apr 2020 7:59 PM
Article: Hydrocarbon Processing March 2020, Improving Plant Operations with Control Valve Simulations, by Reid Youngdahl(Emerson) and Luke Novak(Emerson)
0 Replies
mark.nymeyer
30 Mar 2020 1:24 PM
Article: Hydrocarbon Processing November 2019, Ball Valves in High Temperature Applications, by Jason Jablonski (Emerson) and Wade Helfer (Emerson)
0 Replies
mark.nymeyer
23 Mar 2020 9:14 PM
Article: Select the Right Valves for Adsorption Processes, by Keith Nehring: Chemical Processing March 2020
0 Replies
<
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.