Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5479 subscribers
Views
9241 views
Users
0 members are here
Modbus OPC
Recent DeltaV Community Connect Discussions
Eddie Villarreal
20 Jan 2026 1:53 PM
Does a PID parameter I_HOLD exist?
3 Replies
Nayel
16 Jan 2026 8:11 AM
Windows 10 reinstall / Dell 7920
1 Reply
Nayel
15 Jan 2026 8:53 PM
Deltav operate | Grafic
0 Replies
Jesse Delanoy
15 Jan 2026 1:22 AM
v15 Multi-node Development System Virtual Controller Communication Issues with Mimic
0 Replies
Kirill
12 Dec 2025 3:33 PM
Corrupted database recovery
5 Replies
<
>
Similar Posts
AMS interface with HART devices of 3rd Party Systems thru Modbus TCP in PK Controllers
DeltaV Reporter Excel Add-in connecting thru wrong IP
How can Function Keys (F1 thru F12) be defined differently for DeltaV workstations in the same system?
Can the same PK physical port be used for both Modbus TCP and OPC UA?
OPC Communication between DeltaV OPC and third party OPC (Triconex) - DeltaV OPC Remote
Share
Not Answered
Modbus thru opc
Please explain how to connect Modbus thru OPC.
Modbus OPC
1 Reply
Former Member
27 Jan 2018 6:57 AM
You would probably need to use a 3rd party application like kepware which has modbus interfaces for opc. I think you would then need to use an opc mirror application to link the kepware opc server to the deltav opc server.
I would have thought it would be easier to use a deltav serial card and connect direct to deltav using the modbus protocol rather than use opc.