Delay in Switching to Backup controller

We had a controller fail and it took almost a minute (50 seconds to 1:20 to switch over to the backup. It caused the plant to shutdown. What would be some of the causes of taking so long to switch to the backup?

1 Reply

  • That sounds more like a controller restart than a failover.  What was the status of redundancy in diagnostics?  What is it now?

    What was the cause of the suspected failure, power supplies?