Hello everybody,
I need to restore events to event chronicle. Our System is running with History server 1 and 2 + Backup Server (ArcServ).
I've restored a Backup file with ArcServ, it works so far. The restore file contains one folder per Station (PPlus, Hist1,Hist2....).
In the Hist1 folder I've found "DVEventJournal", wich contains for example "SVHST1#20130120120008.BAK".
I tried to open this "SVHST1#20130120120008.BAK". with "Restore" in the Event Chronicle Administrator. But nothing hapends.
What should I do to "convert" this ".BAK " to ".mdf".
Thank you for your help.
Have a nice Week end!
Christophe.
In reply to Steven Estes:
Thanks a lot!
It works, I've retried step by step and the data are now on the the system.