Deltav Continuous Historian

Historian properties

Max Historian Size :10000MB

Enable max historian span 7 days

historian data set 600 MB

Enable Dataset time span :monthly

Data set export enabled

Historical data entry enabled

Question is with the existing setting my active dataset is not completing using its storage capacity.I have to regularly extend the datasets otherwise there will be no continuous history of tags (broken trends).

Please suggest me how to resolve this issue.

1 Reply

  • Your spans are set for monthly, yet your max historian span size is 7 days….I would say that is your problem.
     