I have a configuration that includes a DeltaV ready 1420 Smart Wireless Gateway acting as a node in the DeltaV Control Network.
I want to map some registers using MODBUS TCP from the Gateway to be used in the Control Studio and Graphics.
Please advice on the procedure.
Why use Modbus?
The values comes trough Wireless HART ?
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
[email protected]
In reply to Niklas Flykt:
We are trying to read values using MODBUS TCP to test compatibility.
Readings are also available from the IO Channels as this is a node in DeltaV Network.
The values are coming from Wireless HART , you are rite.
In reply to mohdismail.khan:
www2.emersonprocess.com/.../00809-0600-4420.pdf
starting from page 43