Hi All
My customer ask me to show the alarms on alarm banner in the order of time, exactly like we can sort the alarm on alarm list.
Some idea? I'm looking for some simple solution, if exist.
Regards
Dawid
You can't change the sorting order of the banner in the manner you suggest. You can embed the alarm list activex object into the banner (you either may need to resize banner to fit everything or toggle visibility of list/banner buttons) dzieba <[email protected]> wrote:
In reply to MPhatale:
Mann,
Will be so easy to solve this problem in this way, look to the standard alarm banner. You are going to show the elements of User alarm table THISUSER/FALMS and I need to change the order of the elements inside this table, there is no animation on priority or on time stamp.
Unfortunately Youssef give me the correct answer, probably there is no way to do this,
May be Jim Cahill can if there is somewhere some hide frs function or global parameter to do this
but I have seen already the frsFactoryGlobals source code and there is nothing
In reply to dzieba:
Dawid, I forwarded your reply to some of my friends on the DeltaV product management team to see if they or any of the developers know about any hidden tricks that they can share.
In reply to Jim Cahill:
Great Jim, I'll wait for news from you
Thank you