We have DeltaV 14.3.1
Project: communicate EIOC with E300 (ethernet).
We need to know the communication parameters for EIOC to communicate with the E300. so far we have achieved with class3 explicit but not sure if this is the correct?
See if these settings will get you started:.
For the signals, they will vary by application. The most important two are probably OUT0 which is an output with a byte/bit offset of 0/0.
This is a typical sanitized signal list I developed for one of our customers. They might not all apply to your situation and you might have to add more based on your needs, but it probably will give you an idea of how to translate the manual to deltav.
Hopefully this helps! Otherwise, please feel free to ask additional questions.
In reply to Matt Forbis:
In reply to Vithal Modak:
Andre Dicaire
In reply to Andre Dicaire:
In reply to Jesse Delanoy: