CSLS Internal Temperature?

The CIOC has an internal temperature parameter in diagnostics.  I do not see a parameter for the CHARMS Safety Logic Solver internal temperature.  Is there any way to get this information?

  • Hi Greg,

    This parameter is not exposed in the CSLS, there's no way to get this info.

    Rgs,
  • In reply to Tadeu Batista:

    Thanks for the quick response Tadeu. Like the CIOC, the CSLS is marketed as a good candidate for field mounted enclosures. I find it pretty disturbing that there would be no means to monitor the temperature of the safety logic solver. Can you comment to the reasoning behind that design? Thanks!
  • In reply to Greg Bayne:

    Absoluterly, it's the perfect candidate!
    The proper way to measure ambient temperature inside the Smart Junction Box, is by adding a RTD sensor, hooking it up to an LS RTD Charm.
  • In reply to Tadeu Batista:

    Well, thanks. That is a good back up plan and sounds like the only option in this case. I am able to monitor a CIOC without the expense of using an RTD and CHARM module, so I was hoping I could do the same with a CSLS. Again, are there plans to add this feature to the CSLS firmware, or is there a particular reason it will not?
  • In reply to Greg Bayne:

    Hi Greg,
    No, there are plans to monitor internal temperature of the CSLS. I understand the cost concern, but if there's a need to monitor the Smart JB internal temperature, that's the right way to do it.
    Rgs,
  • In reply to Tadeu Batista:

    Why do you need to measure the temperature in the panel?

    I think sometimes we do things because we've lost sight of the original reason we monitored temperature in panels. For a long time, control system panels were monitored for temperature because they had active cooling, such as fans and HVAC systems that maintained a desired operating temperature. If the fans failed, or if the HVAC failed, the cabinets could get too warm. Some field panels may have active cooling such as vortex coolers, and again, failure of the cooling system requires detection so that it can be repaired and avoid premature failure of the components inside due to prolonged operation at elevated temperature.

    With the CSLS field enclosures, there is no active cooling. The internal temperature of the enclosure will vary with the ambient air and possible radiant energy if exposed to sunlight. There is no cooling system that could fail resulting unobserved elevated temperature.

    Monitoring the ambient temperature where these enclosures are located can give you the information you need about their operating temperature.

    Assuming you still require temperature measurement inside the CSLS enclosure, there are a couple of other options:
    - use a Thermal Switch wired into the fault relay circuit to a DI. If this exists, then you don't add an additional CHARM and the device is relatively inexpensive.
    - if you have installed a Thermocouple signal, its cold junction compensation value will be indicative of the ambient temperature in the enclosure.

    You could also consider a temporary installation of the RTD solution in that once the overall temperature profile of the installation is understood, and that you are confident there are no adverse operating conditions, the RTD channel could be repurposed in the future if the IO is needed.

    I've been monitoring a CIOC panel for the last 7 years installed outside, equipped with an Outside Ambient RTD sensor, and internal cabinet ambient air RTD sensor and the CIOC onboard temperature sensor. The internal RTD and the Onboard CIOC temperature readings are very repeatable and consistently offset by about 20deg C. This is expected as the CIOC temperature is monitoring the processor temperature. The internal temperature will float about 6 degrees above the outside air at night. During the day, direct sunlight will add up to 10 deg C to the internal temperature. We see max temperatures of about 40 to 45 Deg C from time to time, resulting in a max internal temp of about 60 deg, which drops back to 50 when the sun moves past the building. For most of those hot days, the panel internal temperature is below 50 degC, and for 90% of the year remains below 35 deg C.

    My point is that I know what the internal temperature is by reading the outside temperature and whether it is sunny. If the enclosure were shaded, then one variable would tell me the internal temperature of all installed panels.

    If you have reason to install temperature monitoring, then the RTD is the best solution. My point is not to dissuade you from installing the RTD. I just think that without a clear reason for doing so, we may be consuming IO points that we could use for other purposes.

    Andre Dicaire

  • In reply to Andre Dicaire:

    Hello Andre and thanks for the reply/info. I had actually seen a past post from you explaining the research and the difference seen between the CIOC internal temperature and the ambient around it. I have implemented that reading on several outdoor cabinets and used an offset of 21degC to infer the ambient. Several of the cabinets also house a CSLS. However, we do have one cabinet with just a CSLS. I may go ahead and drop an RTD module on it. I am just simply surprised that the internal temperature of the CSLS isn't made available to monitor while the CIOC does.