Would like to display all active Modelock Overrides.

Is there a graphical way to display all active Modelock Overrides for operations to check at relief time and during the shift?  Can be a report that is activated by the operator but would like the tool at the operator station.  Could create a alarm for each but they must be a way to display ONLY ACTIVE Modelock Overrides on demand.

1 Reply

  • Daryl,

    I have seen other customers accomplish this using a custom alarm with a custom low priority. The alarm priority is low enough to be excluded from the alarm banner and alarm lists. A DeltaV graphic is constructed with the alarm list control, and the alarm list control is filtered to display on the custom low priority. The custom alarm is tied to the Modelock Override bits.