interlink dixell xjp60d to deltav

Hello,
Can someone tell me what are the outputs of Dixell xjp60d on Modbus RTU?
Ia have to connect 12 of them on a Deltav 12.3.
I found
https://www.yumpu.com/en/document/view/ ... ll-devices
and i have
manual http://www.emersonclimate.com/europe/Pr ... P30D_E.pdf
but i can not link one to another. I can not find the parameters described in user manual in the other document.
My question is: the parameters described in manual at page 2/4 section 9(list of parameters) and at page 4/4 ( section 16 general parameters and section parameters) are somewhere in modbus list of xjp60d?
All i can understand from general modbus manual is that i can find probe values at registers 256,257,258,259,260,261 (valid for the first 3 probes-read only so this is input register), and at register 2816,2817,2818,2819 are real time clock (read write) so that will be holding register.
Where are the remaining 3 probes values? It will be the registers 262,263,264,265,266,267?
If i setup up the registers 256,257,258,259,260,261 as holding register would i read anything?
And where is the slave address of device? Is it at register 1 and 2 included in device code?

Can someone give me the modbus description of xjp60d with all parameters/registers?
Thank you.

1 Reply

  • Hello stamate_mircea,

    We apologize for the delay, but it took some time to locate the best persons to answer your question within Emerson Climate technologies. Here is the response I received with contact info as to how to follow up with their business directly to resolve your issue. Best of luck to you!

    "The links you have provided that includes modbus register is now considered obsolete; it is created for XJ500 (which is already obsolete close to 10 years now) In order to properly communicate the Dixell XJP60D in Delta V, you will need to have the correct modbus registers of XJP60D with the correct version (different versions have different registers). The modbus registers are proprietary information and not freely given, thus you will need to contact the Emerson Climate division that manufactured the Dixell XJP60D, you can reach them at [email protected]. "

    Best Regards,

    Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast