WARNING: This script was exported from version 6.3 and has not been processed by the appropriate migration utility to make it compatible with the current version. Hence the import is being aborted.

WARNING: This script was exported from version 6.3 and has not been processed by the appropriate migration utility to make it compatible with the current version. Hence the import is being aborted.

2 Replies

  • You can use the tool called 'ProcessFHX'. The tool is very easy. This tool has to be used after migration utility is processed on FHX.
    the tool will show you all the block, composites, module name used in project. You just need to uncheck the basic block likes AI, PID, AO, DI... and create new fhx and then try to import it.

    I strongly advice to take backup of your original FHX before using this tool.
  • You need to migrate the FHX you are attempting to use using the Migrate Configuration Utility.

    This can be found by going to Start->Al Programs->DeltaV->Engineering->Database Administrator and then double clicking the Migrate Configuration.

    Regards,
    Matt