The post How to Get Rid of Level Oscillations in Industrial Processes first appeared on the ISA Interchange blog site.
The following technical discussion is part of an occasional series showcasing the ISA Mentor Program, authored by Greg McMillan, industry consultant, author of numerous process control books, 2010 ISA Life Achievement Award recipient and retired Senior Fellow from Solutia Inc. (now Eastman Chemical). Greg will be posting questions and responses from the ISA Mentor Program, with contributions from program participants.
In the ISA Mentor Program, I am providing guidance for extremely talented individuals from countries such as Argentina, Brazil, Malaysia, Mexico, Saudi Arabia, and the U.S. This question comes from Luis Navas.
Luis Navas is an ISA Certified Automation Professional and electronic engineer with more than 11 years of experience in process control systems, industrial instrumentation and safety instrumented systems. Luis’ questions on evaporator control are important to improve evaporator concentration control and minimize steam consumption
For an MPC application I need to build a smoothed moving mean from a batch level to use as a controlled variable for my MPC, so the simple moving average is done as depicted below. However, I need to smooth the signal, due there is some signal ripple still. I tried with a low-pass filter achieving some improvement as seen in Figure 1. But perhaps you know a better way to do it, or I simply need to increase the filter time.
Figure 1: Old Level Oscillations (blue: actual level and green: level with simple moving mean followed by simple moving mean + first order filter)
I use rate limiting when a ripple is significantly faster than a true change in the process variable. The velocity limit would be the maximum possible rate of change of the level. The velocity limit should be turned off when maintenance is being done and possibly during startup or shutdown. The standard velocity limit block should offer this option. A properl Save & Exit y set velocity limit introduces no measurement lag. A level system (any integrator) is very sensitive to a lag anywhere.
If the oscillation stops when the controller is in manual, the oscillation could be from backlash or stiction. In your case, the controller appears to be in auto with a slow rolling oscillation possibly due to a PID reset time being too small.
I did a Control Talk Blog that discusses good signal filtering tips from various experts besides my intelligent velocity limit.
In many cases, I’ve seen signals overly filtered. Often, if the filtered signal looks good to your eye, it’s too much filtering. As Michel Ruel states: If period is known, moving average (sum of most recent N values divided by N) will nearly completely remove a uniform periodic cycle. So the issue is how much lag is introduced. Depending on the MPC, one may be able to specify variable CV weights as a function of the magnitude error, which will decrease the amount of MV movement when the CV weight is low; or the level signal could be brought in as a CV twice with different tuning or filtering applied to each.
The ISA Mentor Program enables young professionals to access the wisdom and expertise of seasoned ISA members, and offers veteran ISA professionals the chance to share their wisdom and make a difference in someone’s career. Click this link to learn more about the ISA Mentor Program.
Since the oscillation is uniform in period and amplitude, the moving average as described my Michel Ruel is best as a starting point. Any subsequent noise from non-uniformity can be removed by an additional filter but nearly all of this filter time becomes equivalent dead time in near and true integrating processes. You need to be careful that the reset time is not too small as you decrease the controller gain either due to filtering or to absorb variability. The product of PID gain and reset time should be greater than twice the inverse of the integrating process gain (1/sec) to prevent the slow rolling oscillations that decay gradually. Slide 29 of the ISA webinar on PID options and solutions give the equations for the window of allowable PID gains. Slide 15 shows how to estimate the attenuation of an oscillation by a filter. The webinar presentation and discussion is in the ISA Mentor Program post How to optimize PID controller settings.
If you need to minimize dead time introduced by filtering, you could develop a smarter statistical filter such as cumulative sum of measured values (CUSUM). For an excellent review of how to remove unwanted data signal components, see the InTech magazine article Data filtering in process automation systems.
My experience is that most times a cycle in a disturbance flow is already causing cycling in other variables (due to the multivariable nature of the process). And advanced control, including MPC, will not significantly improve the situation and may make it worse. So it is best to fix the cycle before proceeding with advanced control. Making a measured cyclic disturbance a feedforward to MPC likely won’t help much. MPC normally assumes the current value of the feedforward variables stays constant over the prediction horizon. What you’d want is to have the future prediction include the cycle. Unfortunately this is not easily done with the MPC packages today.
Often, levels are controlled by a PID loop, not in the MPC. The exception can be if there are multiple MVs that must be used to control the level (e.g., multiple outlet flows), or the manipulated flow is useful for alleviating a constraint (see the handbook). Another exception is if there is significant dead time between the flow and the level.
Thank you for the support. I think the ISA Mentor Program resources are a truly elite support team, by the way, I have already read the blogs about signal filtering.
My comments and clarifications:
Figure 2: New Level Oscillations (blue: actual level and green: level with Ruel moving average)
See the ISA book 101 Tips for a Successful Automation Career that grew out of this Mentor Program to gain concise and practical advice. See the InTech magazine feature article Enabling new automation engineers for candid comments from some of the original program participants. See the Control Talk column How to effectively get engineering knowledge with the ISA Mentor Program protégée Keneisha Williams on the challenges faced by young engineers today, and the column How to succeed at career and project migration with protégé Bill Thomas on how to make the most out of yourself and your project. Providing discussion and answers besides Greg McMillan and co-founder of the program Hunter Vegas (project engineering manager at Wunderlich-Malec) are resources Mark Darby (principal consultant at CMiD Solutions), Brian Hrankowsky (consultant engineer at a major pharmaceutical company), Michel Ruel (executive director, engineering practice at BBA Inc.), Leah Ruder (director of global project engineering at the Midwest Engineering Center of Emerson Automation Solutions), Nick Sands (ISA Fellow and Manufacturing Technology Fellow at DuPont), Bart Propst (process control leader for the Ascend Performance Materials Chocolate Bayou plant), Angela Valdes (automation manager of the Toronto office for SNC-Lavalin), and Daniel Warren (senior instrumentation/electrical specialist at D.M.W. Instrumentation Consulting Services, Ltd.).
About the AuthorGregory K. McMillan, CAP, is a retired Senior Fellow from Solutia/Monsanto where he worked in engineering technology on process control improvement. Greg was also an affiliate professor for Washington University in Saint Louis. Greg is an ISA Fellow and received the ISA Kermit Fischer Environmental Award for pH control in 1991, the Control magazine Engineer of the Year award for the process industry in 1994, was inducted into the Control magazine Process Automation Hall of Fame in 2001, was honored by InTech magazine in 2003 as one of the most influential innovators in automation, and received the ISA Life Achievement Award in 2010. Greg is the author of numerous books on process control, including Advances in Reactor Measurement and Control and Essentials of Modern Measurements and Final Elements in the Process Industry. Greg has been the monthly "Control Talk" columnist for Control magazine since 2002. Presently, Greg is a part time modeling and control consultant in Technology for Process Simulation for Emerson Automation Solutions specializing in the use of the virtual plant for exploring new opportunities. He spends most of his time writing, teaching and leading the ISA Mentor Program he founded in 2011.
Connect with Greg