refresh data slow

i have a problem with the data refresh in the operate.

after some hours i restarted the station, the refresh of data become very slow.

deltav revision is 9.3 build 5224 and i have installed all the hotfix for that revision.

suggestions???

17 Replies

  • When we configure link on picture, we use "Expression Builder".

    You can find there "Refresh Rate".

    Try this.

  • In reply to Roman Kostuniak:

    check also scan rate of your control module(s)

  • Try to run the 'Dumpdatasource" utility. This will tell you, if you have any refresh rate issues.

    You can also run deltaV 'Refresh rate expert' on the graphics (Found in standard 'DeltaV_Picture' operate toolbar).

  • Hi,
    Does this happen for a specific graphic or for all the graphic files?
    Does the perticuler graphic file has an ActiveX control like combobox or Textbox object embedded in it?

    On , amodbobade <[email protected]> wrote:
    >
    >
    >
    >
    >
    > Try to run the 'Dumpdatasource" utility. This will tell you, if you have any refresh rate issues.
    > You can also run deltaV 'Refresh rate expert' on the graphics (Found in standard 'DeltaV_Picture' operate toolbar).
    >
    >
    >
    >
    >
    >
    >
  • In reply to MPhatale:

    i have already run dumpdatasource and result no refresh rate issues.

    it happen for all the graphics.

    i don't have particular graphic object, it's a very simple project.

  • In reply to Riccardo Fassi:

    refresh rate expert already done.

    maybe some problem with graphic driver ATI HYDRAVISION?

    someone told me that i have to disable the pplant lan...could be the cause of my problem?

  • In reply to Riccardo Fassi:

    it's really strange that happens only after some hour after i have restarted the station. seems thet fills some buffer or something like that

  • In reply to Riccardo Fassi:

    in to the log files of dumpdatasources i found something strange:

    # ($) Refresh Rates equal 0 or less than 0.5 or 1 = 0 (RefreshRatesEqualZero = 0   RefreshRatesLessThanMin = 0)

    # (&) Deadbands greater than 60 = 0

    # (!) Tolerance greater than 60 = 0

    # (%) Source and FullyQualifiedSource Mismatches = 0

    # (+) Picture Name Mismatches = 0

    # (*) Objects with No Connections = 0 (1= 0  2 = 0  3 = 0  4 = 0  5 = 0  6 = 0  7 = 0  8 = 0)

    # (?) Bad Datasources = 0

    # (^) Bad DataServer References = 544

    544 bad dataserver references? what does it mean?

  • In reply to Riccardo Fassi:

    Your link should begin with: DVSYS.YOUR_MODULE_TAG.....

    I think you have iFix insteed DVSYS - check this

  • In reply to Roman Kostuniak:

    Do you upgrade your system?

  • In reply to Roman Kostuniak:

    my fault, i checked the flag DVSYS in dumpdatasources. now i get no errors.

    i also upgraded the video driver.

    we will see tomorrow the refresh time

  • In reply to Riccardo Fassi:

    Maybe you have too much links on one picture

  • In reply to Roman Kostuniak:

    The following recommendations may help you to optimize your system performance while implementing a refresh rate strategy.

    Leave the default rate of .1 seconds for the refresh rate of every animation in a picture. Alternatively, use one slow rate for the objects that can have slow updates, and one fast rate (such as the .1 second default) for objects requiring faster updates. Using different update rates tends to result in slower performance.

    Avoid using a refresh rate of 0. This is the fastest refresh rate possible and will, therefore, have the greatest impact on your system's performance.  

    When you modify pictures that were created with early versions of DeltaV Operate, use the Refresh Rate expert to set the update rates for older pictures to .1 seconds or greater.

  • In reply to Riccardo Fassi:

    i also noticed that when graphic slowing down the process SQLSERVR use 3 time the normal amount of ram. normally is 45 mega. when station slow down become 145 mega