Secure TCP on WirelessHart network
Forums
Blog
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent IIoT & Digital Transformation Discussions
Emerson Exchange News
5 Oct 2018 5:13 PM
How Solvay Implemented a Digital Transformation
0 Replies
Emerson Exchange News
5 Oct 2018 3:01 PM
Natural Gas Distributor Saves $1 Million with Wireless while Keeping User Experience Seamless
0 Replies
Mike Boudreaux
5 Oct 2018 2:22 PM
VIDEO: Improving Reliability & Performance with Digital Transformation Technologies
0 Replies
Emerson Exchange News
3 Oct 2018 11:25 PM
Valve-monitoring System Opens New World of Data Flow
0 Replies
Emerson Exchange News
3 Oct 2018 12:10 AM
Secure Connectivity Brings Onsite Insights to Offsite Services
0 Replies
<
>
Similar Posts
IIoT wireless cybersecurity must be addressed up front, starting with selection of a network with the required security features. The article discusses the cybersecurity safeguards built into WirelessHART.
WirelessHART Security Update
WirelessHART Not Affected By WPA2 Security Vulnerability
How to Wire Smart Antennas in WirelessHART Networks
Should 5G Be Your Protocol to Handle Backhaul for WirelessHART Networks?
Share
Not Answered
Secure TCP on WirelessHart network
Hi,
I need some help with this issue.
Who can help here?
Thanks,
Adi
Security Setup
HartTalk
WirelessHART
Secure Tcp
gateway
3 Replies
Jonas Berge
1 Dec 2014 2:01 PM
WirelessHART does not use TCP. That is, there is no TCP between the WirelessHART devices and the WirelessHART gateway. WirelessHART has a number of security measures such as encryption, authentication, sequence number, and key rotation etc. which are always on - i.e. you do not need to do anything special to turn it on.
TCP is used between the WirelessHART gateway and the host (system). It can be secured using SSL per protocol e.g. HTTPS, Modbus/TCP secure, HART-IP secure etc.
AdiTzoref
1 Dec 2014 2:10 PM
Yes, this is what I ment.
I have some questions:
1) How can I make a regular TCP connection between the WirelessHART gateway and the host (system)? (Instead of Secure Tcp)
2) How can I send an authentication details externally and not through the HartTalk program? Because I want to make a connection without the HartTalk.
Thanks,
Adi
Jonas Berge
1 Dec 2014 2:17 PM
In reply to
AdiTzoref
:
What is HartTalk? I am not familiar with this program. Please provide link to website
For Emerson gateways use a web browser and go to Setup\Security\Protocols - there you can enable the application protocols you need
Note that it takes more than TCP/IP to communicate. You need to use an applicaiton protocol like Modbus/TCP, HART-IP, EtherNet/IP, or OPC
HART-IP is explained in these articles:
Hart-IP: Large Scale System Integration
http://www.ceasiamag.com/article/hart-ip-large-scale-system-integration/9526
Smart Sensing: Situational Awareness
http://www.iaasiaonline.com/more.php?id=2222&cat=im
Power of Two - New Wireless Solutions for Plant Operations
http://www.ceasiamag.com/article/the-power-of-two/9121