Recent Valves, Actuators & Regulators Discussions
mark.nymeyer
14 Jun 2021 1:22 PM
Article: World’s First Commercially Available Modal Suppression Device
0 Replies
Amir
29 May 2021 1:12 PM
Problem in sizing 3 way Valve fisher specification manager
0 Replies
mark.nymeyer
23 Apr 2021 7:51 PM
Article: Next Gen Trim Reduces Rotary Valve Cavitation
0 Replies
mark.nymeyer
22 Apr 2021 7:51 PM
Article: Troubleshooting Issues and Eliminating Headaches Related to Control Valves
0 Replies
Aurelien Tissot
17 Mar 2021 2:57 PM
Final Control content at Emerson Exchange EMEA, 29-31 March 2021
0 Replies
<
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.