Recent Valves, Actuators & Regulators Discussions
Jim Cahill
9 Oct 2017 1:05 AM
How Intelligent is your Isolation Valve?
1 Reply
Emerson Exchange News
7 Oct 2017 2:06 PM
How Smart Diagnostics Can Keep your Valves Alive
1 Reply
Emerson Exchange News
7 Oct 2017 1:21 AM
Progress on Predicting Control Valve Vibration Failures
0 Replies
Emerson Exchange News
6 Oct 2017 10:03 PM
Flint Hills Resources boosts production uptime with a unique high alloy valve design
0 Replies
Amr Gado
6 Oct 2017 3:43 PM
VIDEO: Four Benefits of Fugitive Emissions Compliant Pressure Relief Valves
0 Replies
<
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.