Recent Valves, Actuators & Regulators Discussions
Emerson Exchange News
4 Oct 2018 7:27 PM
Seneca Resources Uses Multiport Flow Selectors to Minimize Costs
0 Replies
Jordan Mandernach
3 Oct 2018 11:24 PM
VIDEO: How to Start a Small, Successful Valve Diagnostics Program
0 Replies
Emerson Exchange News
2 Oct 2018 7:59 PM
Nickel Processing Plant Cuts Costs with FieldQ VOS
0 Replies
Emerson Exchange News
2 Oct 2018 12:44 AM
Automated Overpressure Protection Systems Saving Millions for Midstream Operations
0 Replies
Erica Brackman
7 Sep 2018 6:19 PM
What is the Difference Between a Monoflange and a Keyblok Valve?
0 Replies
<
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.