Recent Valves, Actuators & Regulators Discussions
Gerard Nagle
11 Oct 2023 8:37 PM
Difference between ED, ET, ES and EZ
1 Reply
MarcyStevenson
7 Sep 2022 9:38 PM
Article: Rethink Your Control Valve Servicing
0 Replies
MarcyStevenson
15 Aug 2022 6:27 PM
Article: New Technologies Solve Severe Cavitation Problems
0 Replies
mark.nymeyer
1 Aug 2022 6:37 PM
Article: Dangers Posed by Non-OEM Parts
1 Reply
VICTOR HUGO ZABALA
9 Jun 2022 11:34 PM
RV: cotizacion valvulas proyecto endulzamiento de gas Cupiagua
1 Reply
>
Similar Posts
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
Corrosion-Resistant Materials in Chemically-Hostile Valve Applications
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.