Recent Valves, Actuators & Regulators Discussions
Nathan Wilhelm
10 Dec 2018 3:18 PM
Direct-operated Regulators vs. Pilot-operated
0 Replies
Nathan Wilhelm
27 Nov 2018 5:08 PM
How Does a Pilot-Operated Pressure Regulator Work (Part 2)
0 Replies
Nathan Wilhelm
31 Oct 2018 7:30 PM
How Does a Pilot-Operated Pressure Regulator Work (Part 1)
0 Replies
Dianne Eldridge
4 Oct 2018 11:19 PM
Quick & Cost-Effective Solutions for Valve Actuation
0 Replies
<
Similar Posts
What happen when an 67CF fails?
FIELDVUE DVC6200 to FEEDBACK HART Conversion
valve position transmitter Vs DVC inbuilt position feedback
Providing Operators Process Control Valve Position Feedback
Providing Operators Process Control Valve Position Feedback
Share
Not Answered
What is happen when FIELDVUE controller losing the opened position feedback?
What is happen when FIELDVUE controller losing the opened position feedback?
1 Reply
Riyaz Ali
17 Sep 2017 7:36 PM
FIELDVUE has built in travel transducer. If travel transducer for some reason, if travel transducer fails, FIELDVUE Digital Valve Controller (DVC) will automatically revert to pressure control mode, which turns DVC basically into I/P mode. Do you have SOV pneumatically in series with DVC for the shut off valve? If you can please provide your location, we can have Emerson local engineer contact you to go in more details.