if you have a 67CF on a control valve, and if it fails in such a way, so that instrument air (IA) supply pressure, 7 bar, is supplied to the positioner.
Would this mean that when the positioner got to the end of its travel, that when it kicked over to full pressure on the diaphragm, that the actuator could see the full IA pressure on the actuator.
For the 657 and 667 actuators, this would exceed the maximum allowable diaphragm pressure, for example, 657 size 46/46i is only allowed to 3.4bar.There are notes associated with it, that discuss that the maximum allowable diaphragm pressure "Its purpose is to allow for typical regulator supply settings and/or relief valve tolerances."
The thing is that I've never seen relief valve between the airset and the positioner. I know that there is the 67CR, but the relief on it doesn't seem to be such to prevent supply pressure on the positioner.
Frans Martens
‘The Other Ways’
Consultant Field Instrumentation and Systems