Change Level (AC to HC) in DVC6010?

Hi all, I received this question on the Emerson Process Experts Facebook page:

good morning... is it possible change the level (AC to HC) in dvc6010
??
thanks

I appreciate any insights you may have.

2 Replies

  • Yes – through ValveLink and a device level stepup dongle.
     
    From: Jim Cahill [mailto:[email protected]]
    Sent: Friday, January 18, 2013 4:17 PM
    To: [email protected]
    Subject: [EE365 Valve Controllers & Positioners Track] Change Level (AC to HC) in DVC6010?
     

    Hi all, I received this question on the Emerson Process Experts Facebook page:

    good morning... is it possible change the level (AC to HC) in dvc6010
    ??
    thanks

    I appreciate any insights you may have.

  • In reply to John Fuller:

    By the way, FIELDVUE Instrument Level StepUp is chargeable. You'll need to contact your local Fisher Sales Office or Sales Representative.

    Instrument Level StepUp  Instrument
    AC to HC  DVC2000 / DVC6000 / DVC6200
    AC to AD  DVC2000 / DVC6000 / DVC6200
    AC to PD  DVC2000 / DVC6000 / DVC6200
    HC to AD  DVC2000 / DVC6000 / DVC6200
    HC to PD  DVC2000 / DVC6000 / DVC6200
    AD to PD  DVC2000 / DVC6000 / DVC6200
    FD to AD  DVC6000f(1) / DVC6200f
    FD to PD  DVC6000f(1) / DVC6200f
    AD to PD  DVC6000f(1) / DVC6200f
    1. Note only applicable to DVC6000f firmware 1.2 or higher.