Calculations for Sizing Control Valves

A Fisher brand technical paper on Valve Sizing Calculations shows the traditional and standardized calculations for properly sizing pressure regulators and valves. The traditional method uses equations designed by Emerson based on the performance of these valves and regulators.

Traditional and Standardized Valve Sizing CalculationsThe paper explains that improper sizing can be both expensive and inconvenient. A too small valve will not pass the required flow, and the process will be starved. An oversized valve will be more expensive, and it may lead to instability and other problemsIn the traditional method, valves used in liquid service are sized with the equation:

Q = Cv √(ΔP/G)

where:
Q = Capacity in gallons per minute
Cv = Valve sizing coefficient determined experimentally for each style and size of valve, using water at standard conditions
ΔP = Pressure differential between upstream and downstream
G = Specific gravity of fluid (water at 60degF = 1.0000)

The paper addresses other factors, such as corrections for the fluid’s viscosity. Using the fluid’s Reynolds number and correction factor, F, from the paper’s viscosity correction nomograph, the predicted flow rate and pressure drop can be calculated.

The paper also discusses conditions to consider including flashing and cavitation and choked flow. For proper sizing the first step is to calculate the required Cv by using the sizing equation. The ΔP used in the equation must be the actual valve pressure drop or ΔPallow, whichever is smaller. The second step is to select a valve from the manufacturer’s literature with a Cv equal to or greater than the calculated value.

For gas or steam service, the sizing equation is:

QSCFH = 59.64 Cv P1 √(ΔP/P1 ) √(520/GT)

60degF from the liquid sizing equation corresponds to 520 degrees on the Rankine absolute temperature scale. The specific gravity of air at 60degF is 1.0. An additional factor can be included to compare air at 60degF with a specific gravity (G) and absolute temperature (T) for any other gas. The equation also converts from the liquids sizing equation in gallons/minute to standard cubic feet per hour. P1 is the inlet pressure.

Read the paper for more information on critical flow limitations, and compressibility effects at increased pressure drops. It also includes adaptions for steam and vapors, an equation for steam below 1000 psiq, and sizing summary. While these equations are for the traditional sizing method, the paper also includes equations for standardized calculations.

Refer back to the Pressure Drop across Control Valves blog post for a basic understanding of the effects of these pressure drops.

The post Calculations for Sizing Control Valves appeared first on the Emerson Automation Experts blog.