DeltaV S serie// Backup Recovery
Dear All,
Hope this email finds you well. I need your help/advice about a back-up recovery of the Delta V program and graphics.
Could you please advice by a simple procedure, I would be grateful.
Thanks for your Support
1 Reply
Jason.Brumfield
12 Jan 2021 6:40 PM
Emerson has a backup and recovery solution, it is customizable and very easy to use. Recommended to be on a non DeltaV server. If that is more than you are interested in, at a minimum export your database daily, backup up your graphics, event chronicles & history files at a minimum.
www.emerson.com/.../backup-recovery-product-data-sheet-en-56972.pdf