How I initiate manual switchover of redundant controller with deltaV diagnostics ?
2 Replies
Hassan.hameed
7 Jun 2020 2:06 PM
Hi
First should be in sure that all redundant parameter status is good when you press on standby controller show these parameter after that check the communication of standby controller and go to the standby controller and right click select switch over and accept the popup message that appear to you now the switch over process is began and check the led for controller it start flash and after that it check after few second in diagnostic you can find it done ,be careful when do that to avoid any trip in plant.
krishna sen
7 Jun 2020 2:30 PM
Thanks a lot.