Emerson Exchange 365
Search
User
Site
Search
User
Replies
2 replies
Subscribers
5474 subscribers
Views
11513 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Rishi
1 Apr 2025 8:04 AM
Best Practices for Thin Client Time Synchronization – Seeking Experiences
0 Replies
GaryL
30 Mar 2025 5:39 PM
VIM 2 and Modbus TCP/IP S-Series Controller
8 Replies
LostEngineer0
7 Mar 2025 4:39 PM
Left mouse click problem
2 Replies
dikshitsh
6 Mar 2025 4:50 PM
Unable to restore Pro plus database from Restore option available in DV database Administration
4 Replies
Kent
5 Mar 2025 1:57 PM
Version 15 FP2 and Rockwell
4 Replies
<
>
Similar Posts
DeltaV switchover Problem
Redundant controller and switchover
Redundant CIOC and EIOC Behavior on Switchover
DeltaV Batch Executive Redundancy Switchover
Switchover during Total CTRL Download
Share
Manual_ switchover
How I initiate manual switchover of redundant controller with deltaV diagnostics ?
2 Replies
Hassan.hameed
7 Jun 2020 2:06 PM
Hi
First should be in sure that all redundant parameter status is good when you press on standby controller show these parameter after that check the communication of standby controller and go to the standby controller and right click select switch over and accept the popup message that appear to you now the switch over process is began and check the led for controller it start flash and after that it check after few second in diagnostic you can find it done ,be careful when do that to avoid any trip in plant.
krishna sen
7 Jun 2020 2:30 PM
Thanks a lot.