Emerson Exchange 365
Search
User
Site
Search
User
Replies
6 replies
Subscribers
5475 subscribers
Views
31139 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
knucklhead90
22 Feb 2026 5:27 PM
DeltaV Alarm Help License Subscription
1 Reply
TreyB
19 Feb 2026 1:21 AM
Live-Control Tag vs Multilanguage String
2 Replies
IntuitiveNeil
12 Feb 2026 3:42 AM
Small HCI host (SE2761V1 based on R660xs) dropped from Emerson DeltaV Product Line Up.
1 Reply
Abdul Samad
30 Jan 2026 5:51 AM
VIM2 Communication issue
3 Replies
István Orbán
29 Jan 2026 9:35 AM
Parameter Value Recovery
1 Reply
<
>
Similar Posts
Extract the logs on an SLS with telnet
Fwd: Net work binding when using 4 NIC
Emerson Exchange 2019 DeltaV Controller and I/O Hardware - Product Update sessions
Be sure to get to the DeltaV roadmap sessions
Control Studio Phantom session issue
Share
Fwd: Telnet session with DeltaV Controller
From:
krishna sen
<
[email protected]
>
Date: Sun, May 10, 2020 at 12:19 PM
Subject: Telnet session with DeltaV Controller
To: <
[email protected]
>
Dear all
Please let me know how can i open a telnet link with MQ controller and look in the Hardware event log ?
6 Replies
Hassan.hameed
10 May 2020 9:06 AM
You can go through diagnostic and select the required controller and right click select telnet after that follow list appear
krishna sen
10 May 2020 9:40 AM
Many many thanks for reply. Can I open telnet link with controller through command prompt ? If yes then what is the linking procedure.
Hassan.hameed
10 May 2020 9:53 AM
In reply to
krishna sen
:
No you cannot only from deltav explorer diagnostic can access to the telnet
krishna sen
10 May 2020 10:21 AM
Thx
Lun.Raznik
11 May 2020 3:41 PM
In reply to
krishna sen
:
telnet IP should work. For example, if IP of the controller is 10.4.0.10, then telnet 10.4.0.10 will open session to the controller.
Jason.Brumfield
16 May 2020 3:44 PM
as an adder, if you have redundant controllers, you have to drill down to the standby in diagnostics to remote the non active controller, each one has it's own telnet logs.