ASCO 580 Charm Node Configuration

Has anyone worked with CHARMs and in particular with the ASCO 580 CHARM Node for Solenoid Valves?
 
I have a question on configuration of CHARMs with this node. This node does not require a CHARM baseplate or individual CHARMs, instead the node is all inclusive. Therefore I am wondering if anyone has configured it previously and if so do they know how the CHARM addressing is configured?
 
1) Does it start at the last CHARM i.e. CHARM 96 and work backwards?
2) Does the CHARM number start at the next available baseplate i.e. if we have 2 baseplates (24 CHARMs) and then a 580 CHARM Node is the first valve on charm 25?
3) Does it start at the last baseplate i.e. CHARM 84 and work forwards?
4) Is it configurable on the ASCO node itself?
 
I think it is option 1, but I can't find anything online to confirm it.
  • Donal,

    I do not think it is configurable, but it depends on how many solenoid valves are connected to the ASCO 580 CHARM module. The valves will occuoy the last addresses of the CIOC. For example of there is 12 valves, it will be on address 8, if you have 24 valves it will occupy address 7 and 8. If more valves are included it will occupy more addresses up to 5-8 if there are 48 valves connected.

    Thanks,
    Rune
  • In reply to Rune Reppenhagen:

    Rune,

    Thank you very much for your reply.

    Based on the above I assume that if there was one valve it would be on address 8 and would be the last CHARM, CHARM 12 on this address?

    Thanks,

    Donal
  • In reply to Donal Costello:

    If memory serves me here, the hardware have 12 soleniod valves. So can pick one of the 12.
  • Hi Donal,

    Don Launder here from ASCO. Let me see if I can shed some light to help out.

    1) As Rune has pointed out above, the manifold always starts counting back from what would be baseplate 8 in an all CHARM I/O setup.
    2) No - We always start from "baseplate" 8 and work backward. this allows for expansion of either I/O or Valve. I put baseplates in "" becasue we don't physically occupy a baseplate, as you pointed out in your OP, but it is virtually taking up those 12 bits on the bus
    3) Again as Rune has indicated a typical 12-station manifold would look something like this in the DeltaV addressing: 8-12, 8-11, 8-10, etc. to 8-01.
    4) There is some degree of configurability within the node itself including: baseplate numbers the manifold will occupy, the ability to flip the counting, and the ability to flip the banks (our term for refering to the "baseplates we occupy).
    I can send you the Tecnical Manual if your interested in learning more. Email me here: [email protected] - Typically I'd send you a link, but we are migrating the page now and I had some issues finding it.

    Don Launder

    Director, Global BD & Strategic Accounts - Hybrid

    Emerson Automation Solutions

    [email protected]

    (603) 491-1477

  • In reply to Don Launder:

    Hi All,

    Thank you for taking the time to answer. I found your responses very helpful. @Don, I will send you a separate email.

    Thanks,

    Donal