DELTAV OPERATE TAKES LONG TO OPEN AND SOMETIMES DOESN'T OPEN
DLL file loading failed while opening operate in configure/run mode in DV version 13.3.3
DeltaV Operate not opening for more than one user
How to Open DeltaV Control studio for one module from DeltaV operate by using VB script?
Where is the "Export to DeltaV Live Toolbar" Button in DeltaV Operate (Configure)?
Share
DeltaV operate and DeltaV configure not open
Dear All
I am using DeltaV 10.3 from last three years.But now I am facing a problem in EWS. DeltaV explorer and control studio are working fine but I can not open DeltaV configure and operate.Any idea how to solve this.
Best regards
Debasis
2 Replies
JDWheelis
2 Apr 2020 8:51 PM
Have you had Operate open since you last booted this computer, and now it doesn't open? If so, check in Task Manager for a process named Workspace. If it exists as a Windows process, use Task Manager to End task, then launch DeltaV Operate.
If Workspace doesn't exist as process, and you haven't recently, a computer reboot may help.
debasis sasmal
3 Apr 2020 4:22 AM
In reply to
JDWheelis
:
Thanks for the reply. Yes, DeltaV operate working fine before rebooting the workstation. I also check that when I try to launch deltaV operate then workspace. exe is open in task manager but after a short period of time this .exe process automatically stop. I several times reboot my system but no luck.