Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
2 replies
Subscribers
5476 subscribers
Views
10846 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
frankfu
17 Aug 2022 2:49 PM
Fuzzy logic control in DeltaV
13 Replies
Steven Cox
15 Aug 2022 1:18 AM
Is the "Gauge" GEM missing from the DeltaV Live PCSD Library?
13 Replies
Randy Pratt
12 Aug 2022 12:47 PM
Microsemi (AKA Symmetricom) S250 and other devices will suffer a rollback issue on 17-SEP-2022 to 18-SEP-2022 transition
2 Replies
Bruce Rourks
11 Aug 2022 4:55 PM
Faceplate for secondary loop
7 Replies
frankfu
10 Aug 2022 9:11 PM
is it possible to display the control horizon in MPC operate Pro? if yes, how to enable it?
3 Replies
<
>
Similar Posts
Is there a way for a picture to move on a value or condition?
Keeping Hydrogen Moving: Secure, Integrated Pipelines for the H₂ Value Chain
Moving test work
Alarm Priority moving
How to identify when HART field value differs from 4-20mA field value?
Share
Not Answered
How to move a value?
How can I move a value of flow totalizer at particular time?
2 Replies
THENNARASU R
17 Mar 2020 9:15 AM
Use TIMER, ACTION or CALC Block
1. Create a Output Parameter "FLOW_STORE"
2. Add TIMER Block and set a specific time
3. Add ACTION Block and write expression like
IF "Timer Output Parameter" THEN
FLOW_STORE := Totalizer value;
END IF
4. once complete, click the "Parse" button. error must be zero then only your expression is fully correct.
gamella
17 Mar 2020 10:08 AM
As "a particular time" do you mean a TOTAL value from the past is required???
If so, you can use a DT block (Dead Time function block). Wiring INTEGRATOR block OUT into DT/IN and setting desired delay X into DT block provides TOTAL value X seconds in the past.
With this you don't have to wait for X time intervals to get a new value. Notice that DT supports download without resetting t's critical values so you don't need to wait for X time after a download to get first "good" value.
DT block also provides some useful functions, as FOLLOW_IN. When this is set to TRUE, DT/IN is passed to DT/OUT without delay, allowing to activate delay programatically. (Check books online to get better understanding on Dead Time Block(